Spa and Hot Tub Tech Support and Parts Sales Help is often available evenings & weekends if you can't get through in the daytime! In Tampa? Stop by our store at 14413 North Nebraska Ave, Tampa, FL 33613! We have the spa parts, pumps and spa packs you need over the counter! Checks, Cash and Credit Cards Accepted! We Export World Wide! Canada, Mexico, Central/South America, Europe!
HOLIDAY SPECIAL
FREE SHIPPING ON ALL SPA PACKS AND FREE LED LIGHT WITH SPA PACK PURCHASE
|
|
| The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
| Indentifying Existing Wiring |
Installing a tub in place of where a previous owner had theirs. So I have 240 with 50Amp breaker/GFCI combo at the main and a 50Amp fused disconnect in the hot tub room. The wiring they used is all the same gauge and all black. The previous owner just cut the cables at the end without labeling them (jerk!). At the disconnect the ground (green) and neutral (white) are labeled but not the two hots (read and black). How does one figure out which hot is which?
Thanks,
Bryan |
| Posted by on 2006-12-17 18:01:20. Michigan (8419) |
|
Hook 'em up to the breaker and meter them out. You'll have to leave either the ground or neutral disconnected, so you don't confuse the two, and you will be able to isolate which is neutral and which is ground. It doesn't matter which hot is which, but ground and neutral can make a difference. |
| Posted by on 2006-12-17 18:51:45. SW Florida (8420) |
|
Thanks Swine
>It doesn't matter which hot is which, but ground and neutral can make a difference.
You're saying I don't need to differentiate between the two hots (usually labeled red and black)? If so, I'm set. I can see the ground cable both because it's labeled green and because they have it grounded to the disconnect box. The neutral is also marked white and passes through the disconnect box. The remaining two wires are unlabeled and go through 50 Amp fuses in the disconnect box.
Does that make any sense, breaker, gfci, AND fuses? Maybe they got a deal on that disconnect box since it's the same as my A/C.
Thanks again,
bryan |
| Posted by on 2006-12-17 21:31:00. Michigan (8425) |
|
That is correct, hots do not matter.
The breaker in the house panel is adequate since it's GFI, and the disconnect near the spa location is just fine. It doesn't need to be fused, but being fused won't cause a problem, as long as the fuse contacts remain clean and corrosion free. The disconnect is there because code requires a disconnecting means for the tub, no closer than 5 feet from the nearest inside edge of the hot tub, and in plain sight. |
| Posted by on 2006-12-18 03:39:59. Albert Lea, MN (8431) |
|
Thanks charger. |
| Posted by on 2006-12-18 08:11:03. Michigan (8433) |
|
| | | The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
Note: Prices and Specifications subject to change without notice
|
|
|
Are you in the Tampa Bay area? Visit Our Store! 14413 N Nebraska in Tampa Florida!
| Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681 Tech Support: 1-813-235-4574 |
|
|