Spa and Hot Tub Tech Support and Parts Sales Help is often available evenings & weekends if you can't get through in the daytime! In Tampa? Stop by our store at 14413 North Nebraska Ave, Tampa, FL 33613! We have the spa parts, pumps and spa packs you need over the counter! Checks, Cash and Credit Cards Accepted! We Export World Wide! Canada, Mexico, Central/South America, Europe!
HOLIDAY SPECIAL
FREE SHIPPING ON ALL SPA PACKS AND FREE LED LIGHT WITH SPA PACK PURCHASE
|
|
| The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
| wire question |
OK here is what I would like to do.
•From Main electric box in basement run UF 6/3 W G wire from a 240 volt 50 amp circuit breaker (non- GFIC) to the outside wall, about 12 feet.
•Go through wall into PVC conduit which will be located under the deck, attached to the joist, the run is about 12 additional feet.
•Conduit will go to a SPA disconnect panel, located on the deck railing, that has 240 volt 50 Amp GFCI protection. Note this is a 240 50 amp GFCI, not a GFCI circuit Breaker (see this web site: http://www.spadepot.com/Merchant2/merch... ode=BX8001 to view this disconnect panel)
•The SPA Disconnect Panel is located 6 feet from the spa.
•From the SPA Disconnect Panel I will run 4 separate (3 plus ground) #6 THHN wires in conduit to the spa.
I want to use UF cable so that I do not have to run conduit in the basement (pain in the neck). Is this allowable. I have seen different info on the web ranging from the ground not being insulated in UF Cable so it is not allowable to it is not allowable to have UF cable in conduit for a whole outside run.
Spa Requirements 220 volt 50 amp dedicated circuit, number 6 3 wire with ground, Use THHN copper wire only
Any advice? Thanks |
| Posted by on 2006-11-01 07:21:53. (7701) |
|
The wiring should be ok, however I cringe at that type of spa disconnect. It isn't a true fully GFI protected circuit. What it does is uses a small 120V GFI breaker to operate a contactor in the panel. The theory is that if there is a ground fault, it will trip the small breaker, releasing the contactor, thus disconnecting the whole spa. In reality, there can be an instance where the contactor gets welded in the CLOSED position, from arcing, and no matter what that little GFI breaker wants to do, the spa is being fed full power. So, situation is this: Heater shorts out, contacter welds since a shorted heater draws infinite amps (enough to weld), heater opens to the water, GFI breaker senses this and tripps, but low and behold, the heater is still feeding deadly current into the spa, giving the occupants one heck of a ride. |
| Posted by on 2006-11-02 18:22:44. Albert Lea, MN (7725) |
|
Thanks Charger 1. I appriciate your time and input. What is interesting to me that in my research on the web and in speaking to electricians I get different answers to the same questions. Some love the GFCI SPA disconnect and hate the GFCI Breaker and others are the other way. Same with the wire set-up. Makes it hard to know what to do. Thanks again. |
| Posted by on 2006-11-02 20:08:31. (7730) |
|
Personally, I would rather rely on a single device, rather than the 3 required in your applicaton. If any one fail, the whole system can be left unprotected. With a single GFI breaker, they generally fail in a protected state, as long as it is a QUALITY breaker (spit on cutler-hammer here) |
| Posted by on 2006-11-02 21:00:17. Albert Lea, MN (7731) |
|
| | | The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
Note: Prices and Specifications subject to change without notice
|
|
|
Are you in the Tampa Bay area? Visit Our Store! 14413 N Nebraska in Tampa Florida!
| Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681 Tech Support: 1-813-235-4574 |
|
|