Home |  Spa Forums |  Terms |  Contact Us |  Shipping Inquiry |  About Us |  Jobs |  Visit Our Store! 14413 N Nebraska in Tampa Florida!  
 Sales: 1-866-364-9681   Support: 1-813-235-4574    14 Online  
We're Open! Tuesday Evening Sales & Tech Help Available Now! 8:44 Pacific, 7:44 AST, 5:44 PM HST, 1-813-235-4574
Unsure about your purchase? We're available to answer your questions now. Give us a call to help complete your order. If you're in the Tampa area, come see us at our store. We're located at 14413 North Nebraska Ave! We have the spa parts, pumps and spa packs you need over the counter! Checks, Cash and Credit Cards Accepted! We Export World Wide!
Forums  > Spa & Hot Tub Electrical/Electronics  > Spa & Hot Tub Electrical/Electronics  >
Click to Check Out from Spa Parts Net, Visa MasterCard Amex Discover Accepted
Spa Filters
Parts by Spa Brand
Spa Parts & Equipment
Spa Parts On Sale!
Popular Spa Parts
Spa Packs, Controls

Electric Heaters / Parts
Spa Pumps
Pump Motors
Pump Parts
Blowers / Motors
Ozone Generators
Chlorine Generators
Gas Heaters / Parts

Spa Replumbing
Air Buttons
Accessories
Air Knobs / Valves
Electrical Parts
Circuit Boards
Jets
Control Panels
Lighting / Illumination
Electronic Temp Sensors
Filters
Plumbing Parts
Thermowells, Heater
Pillows
Hot Springs Parts
Reference Catalog
Waterway Jets Catalog
Search Spa Parts:
Search Spa Filters:

The information contained in this forum is from SpaForums.Com and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk!
Connecting Spa Disconnect when spa already has GFI circuit HELP PLEASE!

Hello everyone,

I have the electrician at my house and he is hooking up my 240v spa 50amp. This is a new home and I had them wire a 50amp circuit to the back of the house about 20 ft. from where the spa is. The 50amp breaker in the main panel is NOT GFI. However the built into the spa electric panel is a GFI.

My question is will I still need a Spa disconnect on the wall about 15 ft. away from it as per code? Also should it be a fuse disconnect or GFI? The electrician is saying that it can't be GFI because it will cause to much resistance and pop the breaker and I believe him because I connected a GFI spa disconnect and it popped the breaker. With the fuse disconnect it worked fine.
So the Electrician who is Licensed says that since my spa control panel has a GFI then he doesn't need to place a SPA Disconnect GFI or Not.

What do you guys think? Is this up to code in California?

Thanks,

Mike

Posted by on 2006-08-11 13:35:21. (6546)

There is no such animal as too much resistance because of a separate gfci breaker.

Yes you are required to have a separate disconnect.

Like this:

Main box -----> Disconnect -----> Hot Tub.

If you connected a gfci as the disconnect breaker and it tripped a/the breaker then it was wired incorrectly.

And I would never trust a built in GFCI in a spa control as they will normally fail early in the game, and... when they do, they fail in the ON position, leaving the spa powered up with no protection.

Posted by on 2006-08-11 13:53:11. Metro Atlanta, Georgia Region (6547)

Let me ask you this. If the run is about 30-40 ft. and I'm running 240v with 50amp breakers what Gauge wire will I be safe with?

Mike

Posted by on 2006-08-11 14:46:04. (6553)

About half of these things I see in the field are done with 8 gauge copper, which really isn't right as far as a 50 amp installation.

They should be 6 gauge.

Posted by on 2006-08-11 14:53:11. Metro Atlanta, Georgia Region (6555)

If 8gauge is already done will it be ok? Or should I have the Electrician come back and rewire 6 gauge?

Thanks again,

Mike

Posted by on 2006-08-11 15:01:05. (6557)

I'll leave that decision up to you. Local code will dictate what should/can be installed. The NEC bases all of this on 80% of current carrying capacity, so the sizing of 6 gauge is intentionally overrated. Here's one chart... http://www.allaboutcircuits.com/vol_5/chpt_3/2.html That said, I've yet to see a house or spa burn down because of 8 gauge wire on a 50 amp circuit. You didn't say anything about the maximum current rating of your spa... and that will figure into all of this. If there isn't one listed (or it's disappeared), you'll need to respond with all of the voltage & amperage ratings you find on your pumps, blower, etc.

Posted by on 2006-08-11 15:25:17. Metro Atlanta, Georgia Region (6558)

The sub panel is a must. We see more than half the 240v GFCI hook ups are done wrong -- and this is by licensed electricians. The number one problem we see is they miss wire the Neutral wire--it cannot be a ground if a GFCI is used.
If a GFCI breaker is used in the sub - the white Neutral wire is a LOAD NEUTRAL -- it must be hooked to the breaker-- not the buss bar or wire nut to another wire of any sort.
If you have a GFCI on the spa pack -- they usually monitor one side of the incoming power-- ie 110v not 240v like the sub and breaker.
I have never seen a properly wired GFCI cause to much resistance and trip because of it, thats not how they work. Even big shot electricians dont undertsand how these are suppost to work -- thats why we see grounded LOAD NEUTRAL wires all the time.

If it was me i would run the GFCI load center - fancy name for the sub box with a GFCI. near the tub as your shut off box.

Posted by on 2006-08-13 01:08:40. (6591)

All,

I have pictures of my wiring that I took and are very clear. I also have them of the spa rating.

The spa is 240v, 40amp, Frequency 60

Looks like the Electrician used 10gauge wire that is Gasoline resistant etc...etc..

I compared the wiring to the 4-circuit Spa Panel on Eaton Cutler-Hammer site and everything looks right according to their drawing.

Why would only 1 of the post on the 50amp circuit on the house breaker trip and the other stay on? IS it possible that it's bad??? Should I replace it?

Please email me with responses.

I have included photos of the SPA Disconnect wiring as well as info from the spa.

If you can't see the pics on here let me know and I can email them.

Thanks all for your help!

Mike

Posted by on 2007-01-06 17:19:44. (8623)

My greatest experience with this situation is that one side of the breaker - the wires are not tight enough, which over heats that one side - (this is usually the L1 side).

Double check the tightness of the hold down screws.

If they were loose, and then re-tightened and then it still trips, then it's time to replace that breaker. Usually about $8 at home depot.

Posted by on 2007-01-06 17:58:41. Metro Atlanta, Georgia Region (8624)

Great...thanks for the info. I'll check the breaker to see if there is a screw loose anywhere and then if not I'm going to go buy one. That was my original plan.

Thanks again,

Mike

Posted by on 2007-01-06 20:00:30. (8625)

Quote:

The sub panel is a must. We see more than half the 240v GFCI hook ups are done wrong -- and this is by licensed electricians. The number one problem we see is they miss wire the Neutral wire--it cannot be a ground if a GFCI is used. If a GFCI breaker is used in the sub - the white Neutral wire is a LOAD NEUTRAL -- it must be hooked to the breaker-- not the buss bar or wire nut to another wire of any sort.

I'm using a GFCI center as my disconnect. Are you saying that the white wire from the tub needs to be wire nutted to the white wire from the GFCI but NOT to the buss block? So the only thing going to the buss block is the bare coppers from the house and the tub, and the white wire from the tub terminates at the GFCI? Sorry just a little confused on that <img src=" title="Cool" />

Posted by on 2007-01-25 02:30:42. (8774)

NM Found this convenient drawing. Looks like I have it wired correctly.

Posted by on 2007-01-25 02:38:30. (8775)
Reply New Topic
The information contained in this forum is from SpaForums.Com and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk!
Note: Prices and Specifications subject to change without notice
Click to Check Out from Spa Parts Net, Visa MasterCard Amex Discover Accepted
Search Spa Parts:
Search Spa Filters:
Discussion
General Q&A
FAQs Tips & Help
Installs, Rebuilds, Mods
Troubleshooting Spa/Hot Tub
Spa Photo Gallery
Leisure Items
Hammaka Products.
The Brass Baron
News
Related @ SpaForums
CalSpa Model 6300 control issue...
Update... 11/30/08 I took off the sides to reach the controls and it became all too (more)...

Air Valve Replacement Beachcomber Tub
Hi, I need to replace the air valve on my 2002 beachcomber 530. While looking inside (more)...

3 dots flashing and already replaced the pressure switch
Hi, We have a PDC Spa, actually at one of our rental cabins, and several months ago, (more)...

3 dots flashing and alreay replaced the pressure switch
Hi, We have a PDC Spa, actually at one of our rental cabins, and several months ago, (more)...

Spa pumps turn on and off
Yes, when you turn it on it says FLO and the 1 pump that I turned on it's light was (more)...

Circulation pump wiring issues.
I purchased an E5 circulation pump, and the wiring instructions given to me said that (more)...

Where to buy CalSpa Motor?
Techies- I recently replaced a 6HP pump on a CalSpa, because it had been making a (more)...

ASI Manhattan Spa
Hope you can help, I've just got the above spa, the heating light has been flashing (more)...



Search For Spa Parts, and Hot Tub Parts using part numbers, names, and manufacturer here:
Spa FiltersParts by Spa BrandSpa Parts & EquipmentHot Springs PartsReference CatalogWaterway Jets CatalogDiscussionLeisure ItemsNews
Are you in the Tampa Bay area?  Visit Our Store! 14413 N Nebraska in Tampa Florida!  
Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681  Tech Support: 1-813-235-4574
 
No representations or warranties are made as to the accuracy or completeness of the information contained in this website. Check with a competent professional in your area for assistance.







Powered By: SpaNet