Concerned about the economy? Fix your spa now, most people don't need to buy a new tub! (Save Money $$$) If you're in Tampa, stop by our store at 14413 North Nebraska Ave! We have the spa parts, pumps and spa packs you need over the counter! Monday thru Friday 9-5, Saturday 9-3 We Export World Wide! Canada, Mexico, Central/South America, Europe!
|
|
| The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
| using 30 amp breaker |
I just got a hot tub from a frend, be for we on hooked it I got a amp reading of 28 amps, this was on high speed pump and the heater on, would it be okay to hook up to a 30 amp breaker, reason I'm asking is I have a 30 amp wired 10 feet away, other wise my breaker box is 35 feet away, just trying to save some money on wire, start up is high just for a second, hard to tell around 40 amps happens so fast then gose to 28 amps, thanks |
| Posted by on 2006-10-27 06:06:39. (7560) |
|
Whatever size breaker you have the spa cannot go over 80% of that, so if you a 30-amp breaker your spa should not a total load over 24-amps.
You will also you need check your local codes and the NEC the insure the spa is installed to code. |
| Posted by on 2006-10-27 10:48:13. (7565) |
|
A 40 Amp breaker would definitely be the 'standard issue' breaker for that tub, and like Gary said, be sure it's wired to code.
If your existing circuit is 30 amp I'm assuming that it may have only 10 gauge wire on it? If so, then you'll need to up it to 8 I believe with a 40 amp breaker. |
| Posted by on 2006-10-27 11:10:06. Metro Atlanta, Georgia Region (7566) |
|
my pump is 110 volts chould I go to a 220 volt pump? if it can be done, this is a great lakes spa, 1996, this would put me into the 80% range, plus it would be cheaper to run. thanks |
| Posted by on 2006-10-27 12:39:20. (7567) |
|
you can certainly do that. You'll have to change the common on the pump motor to L2 input instead of Neutral though. |
| Posted by on 2006-10-27 13:38:19. Metro Atlanta, Georgia Region (7568) |
|
If remove the 120-volt pump and install a 240-volt and change the neutral to a common (hot) the GFCI breaker will trip if the system was not setup to do this originally. |
| Posted by on 2006-10-27 18:20:35. (7580) |
|
I wasn't referring to moving the neutral to hot.
Was talking about the common line of the motor itself - that would be removed from neutral then re-connected to L2. |
| Posted by on 2006-10-27 18:57:21. Metro Atlanta, Georgia Region (7585) |
|
| | | The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
Note: Prices and Specifications subject to change without notice
|
|
|
Are you in the Tampa Bay area? Visit Our Store! 14413 N Nebraska in Tampa Florida!
| Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681 Tech Support: 1-813-235-4574 |
|
|