| 2001 cal spa tripping GFCI 50amp breaker |
It is a 2001 Cal Spa Vista hot tub. If I have the jet button in the on position, and go to power up from the GFCI breaker it will turn on. But, if the jet button is in the off position and I go to power up it will trip the breaker. Also when the hot tub is running with the jets on and I go to turn the jets off it will trip sometimes. It seems if the jets have been running for awhile and I go to turn them off the breaker will not trip, but If I go to turn the jets off and they have only been running for a short period of time it will trip. Also, If the jets have been running for awhile and I turn them off and it does not trip, I will check it in a few hours and it will have tripped in that time without touching anything. Also, the hot tub makes good heat, I have had it as high as 105 degrees F.
Suggestions???
From what I have read it is either the motor or heater. The tub makes good heat so I am thinking the motor??? |
| Posted by on 2009-08-06 13:08:31. (17923) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
It sounds more like the heater to me. If the spa is hooked up 110V then the heater won't turn on unless the jet pump is off. You can unhook the heater to test this theory. |
| Posted by on 2009-08-06 14:34:12. (17924) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
It is 220 volt |
| Posted by on 2009-08-06 20:17:53. (17926) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
Disconnect your components one at a time and see if it stays reset.
Sorry, I don't know much about Cal Spas. |
| Posted by on 2009-08-07 09:47:37. (17931) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
I turned the heater all the way down to it's lowest setting without unplugging it. By doing this I beleive I deactivated it. The tub jets turned on and off without throwing the GFCI breaker. As soon as I turned the heater setting to HOT and turned the jets on and off it flipped the GFCI breaker. So it seems the heater is the problem.
Now, is it repairable, or do I need to replace it?? If replacing, where can I buy one cheap? |
| Posted by on 2009-08-07 12:03:00. (17932) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
I have yet to see a heater that is repairable - sorry you have to replace it.
Good Luck |
| Posted by on 2009-08-07 13:07:21. (17933) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
So, I left the jets on over night with the heater set to spa temp.. The temp. settings go off, cool, warm, spa, hot. I woke up and remembered I had left the jets on. I went to go turn them off and the water temp was up to 118 degrees F!!! The reset button for the heater was popped out. I popped it back in turned the heater to off and left the cover off to cool down. The jets and everything seem to still work ok. So I am def. wanting to replace the heater soon. I have about 3 months before freezing temps. and the last thing I want is a cracked shell and pluming. So, are their any walk throughs or how to's in replacing a heater? |
| Posted by on 2009-08-29 15:08:36. (18181) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
I'm not sure on that heater.
If you left the jets on and they ran for a long time the spa can heat up by friction. I have seen them get that hot. |
| Posted by on 2009-08-31 13:13:45. (18211) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
Is it possible the heater does not work at all and the only thing heating the spa is the jets??? |
| Posted by on 2009-09-02 19:14:28. (18238) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
| Quote: Is it possible the heater does not work at all and the only thing heating the spa is the jets??? |
Only if the jets are run for a long time. If you turn on the heater and the gfi trips then it should be a bad heater.
|
| Posted by on 2009-09-03 07:54:48. (18241) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
Where can I buy a new heater for my cal spa online??? |
| Posted by on 2009-09-07 20:19:19. (18266) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
The heater only trips the gfi when it engages with the jets turned off. The heater can turn on and off fine if the jets are running.... |
| Posted by on 2009-10-06 21:34:27. (18571) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
Sorry, I'm baffled - anyone else? |
| Posted by on 2009-10-07 17:33:34. (18586) |
|
Re: 2001 cal spa tripping GFCI 50amp breaker
The Ozone check valve had failed, and the ozone had flooded with water. I took the ozone out and just plugged the line and she works like a champ! I am going to let it dry out for a couple of weeks and then put it back in to see if it works... |
| Posted by on 2009-10-20 12:52:31. (18732) |
|
|