Forums  > Spa / Hot Tub Circuit Breaker or GFCI Tripping Offline  > Spa / Hot Tub Circuit Breaker or GFCI Tripping Offline  >
Click to Check Out from Spa Parts Net, Visa MasterCard Amex Discover Accepted
Spa Filters
Parts by Spa Brand
Spa Parts & Equipment
Spa Parts On Sale!
Popular Spa Parts
Spa Packs, Controls

Electric Heaters / Parts
Spa Pumps
Pump Motors
Pump Parts
Blowers / Motors
Ozone Generators
Chlorine Generators
Gas Heaters / Parts

Spa Replumbing
Air Buttons
Accessories
Air Knobs / Valves
Electrical Parts
Circuit Boards
Jets
Control Panels
Lighting / Illumination
Electronic Temp Sensors
Filters
Plumbing Parts
Thermowells, Heater
Pillows
Hot Springs Parts
Reference Catalog
Waterway Jets Catalog
Search Spa Parts:
Search Spa Filters:

The information contained in this forum is from SpaForums.Com and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk!
Circuit breaker tripping, but heater seems OK

I have a Sundance optima spa, around 1998, indoor. It's wired with a 50A dedicated 230V circuit. The heater is a cylinder maybe 3" in diameter mounted directly on the control box.

After working fine for many years, the breaker started tripping sporadically, then with increasing frequency. Local spa guy came out, pointed out some leakage from each of the two pumps (one 2speed) and suggested replacing them. He wanted to replace the whole units - I decided to just replace the wet ends myself - MUCH cheaper.

Wet ends replaced, no more leaks, but breaker still blows. Seems like if the heater is on, it blows quickly, but if no heat, then it goes for a while (the latter no conclusively proven yet).

I saw some notes here about measuring resistance to ground, but each end of the heater shows infinity to ground. There was about 11 ohms between the two heater terminals. Now I was only able to get to the spa about 15 mins after it blew, so maybe the heater had drained by then?

I also disconnected the electrical supply line from the control unit (with the breaker off). Each leg of the supply line (at the spa) measures about 10-30K ohms to ground. With the supply disconnected, each terminal block on the spa - where the supply line normally connects - showed infinity to ground.

So the spa side looks good from that respect, but should the resistance to ground of the supply line be that low? I'd rather not disconnect things at the circuit breaker end, since then I have to cut power to the house (or work on an open panel).

I don't know that it is blowing due to a ground fault vs. overload, but nothing seems hot, so I suspect a ground fault. Is there a more definitive way to tell? I suppose I could do a current measurement and see what that shows.

I'm running a longer test with no heater on, to see what happens there.

Any suggestions very welcome.

...Mike

Posted by on 2005-04-13 16:06:51. (2300)

So, the pumps were leaking a little water, not electrical current, right?

Anyway, you're usually looking at one of several culprits with this trype of issue, though there are always exceptions.

First, disconnect BOTH heater leads, see if the problem disapears. If not, check for burnt/damaged wires at the main breaker, subpanel, and main terminal block. If they appear fine, see if you have an ozone generator installed. If so, disonnect power to the ozone generator.

Posted by on 2005-04-18 09:12:56. SW Florida (2322)

yes, it was water leaking.

Turns out the problem was at the circuit breaker. Replaced it, and all things look good now. Thanks for the help.

Posted by on 2005-04-18 13:15:19. (2323)
Did you replace the breaker?

mkraley, or anyone else.... Can you elaborate was your breaker in the panel bad. Did you just replace the breaker? I am having similar issues. Recently bought a new heater element. was running great for about 2 months. Now the heater runs for about 10-30 minutes and then cuts off. (Heater light was on entire time till the breaker trips.) If I reset the breaker it'll run for a another 10-30 minutes and trip out again. GFCI circuit near Spa does not trip, and tests out fine. (BTW: I have a Crown Spa with a pneumatic/analog spapack, 220V Heater and 2 speed pump setup with a 15 long stainless 3" Heater at the top backside of the control box. The thermostat is on the left side of the control box. I recently replaced one of the contacters for the heater and it was working great.) Photos here: http://spaforums.com/viewtopic.php?t=3987&highlight= If I turn the heater control way down in temp so the heater never cut's on (I live in Florida) the spa circulates at any speed indefinitely. I have not done any testing on the heater element with ohmmeter but I can if I know what to test for. So I either have some kind of heater problem... or possibly the breaker (or connection) in the panel is bad. I bought the breaker and external GFCI box when I got the spa running about 6 months ago. One more thing.. when the original heater went bad it used to trip the GFCI and the 200A house breaker and not the the 50A panel breaker (2 pole). Not sure if this is related, or is indeed a sign of a bad breaker.. I'm hoping that it might be the breaker since this is a cheap easy fix. breaker breaker... just had to say it a few more times... <img src=" title="Smile" />

Posted by on 2008-01-23 21:12:50. Jax, FL (12414)

There was a bad connection between the breaker and the panel. I think there was some oxidation between the pigtail and the panel screw. This caused high resistance => heat => an even worse connection. The wire was melted.

Posted by on 2008-01-26 11:19:31. (12447)

Thanks. Sorry I did not notice your post was a few years ago....

Is that one thing that can cause what they call a "dead fault"? I have heard that term while troubleshooting the other symptom of the 200A breaker tripping instead of the 50A breaker.

I will inspect/replace the breaker and connection and post results.

Posted by on 2008-01-28 20:59:47. Jax, FL (12462)
It was the breaker

I noticed that when the heater and pump were running that the breaker was warm-hot on the outside of the panel in the house just before it tripped.

I shutoff power to the panel and replaced the breaker and reapplied the power and the problem is fixed. The new breaker does not even get warm after an extended time.

The old breaker which I bought new less than 6 months ago was a little loose when pushed in all the way on the the copper load bar. (my electrician installed it the first time so I did not notice it was loose) This was on one of the hot wire connections at the back of the 50 A breaker. The 6G wires leading off to the outside GFCI box showed no signs of heat, but the back of the breaker where it interfaced the copper load bar had some black dust indicating heat corresponding to the black 6G wire.

The heater uses both poles and more current so this could explain why it was only popping the breaker when the heater was running for a while.

Thanks for your help guys. Hope this helps someone else.
( Disclaimer: working with the Breaker Panel is dangerous, consult with an electrician as I did, if you are unsure)

Posted by on 2008-01-31 11:35:58. Jax, FL (12502)
Reply New Topic
The information contained in this forum is from SpaForums.Com and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk!
Note: Prices and Specifications subject to change without notice
Click to Check Out from Spa Parts Net, Visa MasterCard Amex Discover Accepted
Search Spa Parts:
Search Spa Filters:
Discussion
General Q&A
FAQs Tips & Help
Installs, Rebuilds, Mods
Troubleshooting Spa/Hot Tub
Spa Photo Gallery
Leisure Items
Hammaka Products.
The Brass Baron
News
Related @ SpaForums
Need help with a Balboa VS501Z Retrofit
I am upgrading a 20 year old Spartan Hot Tub with a Balboa VS501Z electronic panel (more)...

Help with an old Vita Spa only half jets are working
I was given an older vita spa that was frozen and had some leaks. I've got all the (more)...

magnetek century lasar pool/spa motor pump
Hi. I have a century lasar pool/spa motor with pump. motor caracteristics: The main (more)...

Sundance Sentry 850 problems
We had a friend who had a sundance spa with the control panel saying sentry 850. He (more)...

blue ridge spa tripping breaker after heater pump replaced??
Let me first start with why I replaced the pump started heating weird,would go up (more)...

New Silentflo 5000 making noise
I just installed a new Silentflo 5000 exact replacement in my 19 year old Hot Springs (more)...

Where to buy CalSpa Motor?
Techies- I recently replaced a 6HP pump on a CalSpa, because it had been making a (more)...

External Pump Corrosion
I have corrosion forming on the outside of my pump. How can I get it off and prevent (more)...



Search For Spa Parts, and Hot Tub Parts using part numbers, names, and manufacturer here:
Spa FiltersParts by Spa BrandSpa Parts & EquipmentHot Springs PartsReference CatalogWaterway Jets CatalogDiscussionLeisure ItemsNews
Are you in the Tampa Bay area?  Visit Our Store! 14413 N Nebraska in Tampa Florida!  
Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681  Tech Support: 1-813-235-4574
 
No representations or warranties are made as to the accuracy or completeness of the information contained in this website. Check with a competent professional in your area for assistance.







Powered By: SpaNet