Concerned about the economy? Fix your spa now, most people don't need to buy a new tub! (Save Money $$$) If you're near Tampa, stop by our store at 17420 N US Hwy 41; in Lutz! We have the spa parts, pumps and spa packs you need over the counter! Monday thru Friday 9-5 We Export World Wide! Canada, Mexico, Central/South America, Europe!
|
|
| The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
| GFCI burning out (one leg) but not tripping |
We bought and installed a new hottub (Pinnacle, Meridian model) http://www.premiumleisure.com/PinnacleSpas/Meridian.html, outside installation. We had an electrician wire it in from the house with a 2-leg GFCI in a box next to the tub. We finally got it running the week before Thanksgiving. It has a 2 speed jets pump, but we couldn't get it to come on high speed. I thought it was a bad pump, but when I put a meter on the black and red wires from the breaker box inside the Balboa Control box inside the tub, I found it was only getting 120v instead of 240. So I tested the breaker box and I had 240v coming into the box from the house, but only 120 on the other side of the breaker.
As it turns out, the GFCI breaker in the box had a bad leg so only 120-volts was going to the pump (and the heater, which now explains why it would lose temperature so quickly when we took the cover off).
Well, guess what, I'm on my thrid GFCI breaker. Each time I put one in, one leg burns out. Something, it seems to me, in the hottub is shorting out and burning up one leg of the breaker. However, it doesn't seem to be a dead short since it's not tripping the breaker, just burning one leg out.
Any ideas ? I can't afford to keep buying 2-leg GFCI breakers..... |
| Posted by on 2008-12-03 15:02:39. (15402) |
|
Re: GFCI burning out (one leg) but not tripping
TRY TESTING THE BREAKER IN YOUR HOUSE PANEL, sounds to me like you have a pair of single pole breakers trying to do what needs to be a double pole breaker. If you have a double pole (two breakers combined into one with a bar across both buttons) you should read 220 or 240 volts across both terminals or 1/2 of that reading from each lug to ground. If you read 220+ across both lugs and it's a "double pole breaker" your problem lies elseware. Good Luck, Howard I'm new to these forums as of today.
LIFE ISN'T ABOUT WAITING FOR THE STORM TO PASS, IT'S ABOUT LEARNING TO DANCE IN THE RAIN |
| Posted by on 2009-02-03 10:00:29. (16049) |
|
| | | The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
Note: Prices and Specifications subject to change without notice
|
|
|
Are you in the Tampa Bay area? Visit Our Store! 14413 N Nebraska in Tampa Florida!
| Copyright © 1997-2009 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681 Tech Support: 1-813-235-4574 |
|
|