Concerned about the economy? Fix your spa now, most people don't need to buy a new tub! (Save Money $$$) If you're in Tampa, stop by our store at 14413 North Nebraska Ave! We have the spa parts, pumps and spa packs you need over the counter! Monday thru Friday 9-5, Saturday 9-3 We Export World Wide! Canada, Mexico, Central/South America, Europe!
|
|
| The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
| GFI tripping intermittently but seems to be load related |
GFI in house trips intermittently but seems to occur when tub is heating and pump comes on at the same time.
It's a 2004 Beachcomber tub with hushpump. GFI circuit breaker is 40 amp 220 v Federal Pioneer in house.
Problem can not occur for 2 months and then might occur twice in the same week, so not sure it's always related to the pump and heater load. We do get a lot of rain...living in the northwest, but I've checked and the pump and heater area are bone dry...have to keep chasing spiders out. Had Beachcomber check it out about 6 months after installation. Pump was replaced and no tripping for about 3 months. then intermittent again. could almost live with the problem except I'm concerned that temperature may drop below freezing when we're not here...then big problem.
no other GFI circuit breakers tripping at panel so appears localized to the hottub.
current opinion amongst team of amateur sleuths (altho' it includes the electrician that installed circuit breaker) is that the gfi circuit breaker is faulty. they're expensive to replace so have been reluctant to rush out and buy one to see if that's the solution..about $220 in Canada. also, thought of bumping it up to 50 amp, as it may not be able to handle surge of pump? which hottub manufacturer was o.k. with in terms of protecting equipment. but Federal Pioneer don't manufacture 50 amp gfi.
any thoughts or suggestions would be welcome. thanks. |
| Posted by on 2007-12-04 00:36:52. (11878) |
|
Well first off I'd leave the spiders be... they eat the other bugs that rodents like to eat... which keeps the food chain at a minimum underneath the spa.
2 things you may want to do....
1. Open up breaker panel and CRANK DOWN on the screws for the main gfci breaker (breaker turned off of course).
2. Unplug the ozonator.
#----------------------------
Then wait to see if it repeats again.
If not, then plug in ozonator again.
Watch and wait...
If it trips then replace the ozonator.
This nuisance tripping can be the death of your wallet.
You may want to go ahead and purchase a digital vom that has a resistance measurement capability above 2 meg-ohms. You can use this to find marginal faults to ground at the tub. I'd do the above 1 and 2, get a meter and do some testing. |
| Posted by on 2007-12-04 01:16:40. Metro Atlanta, Georgia Region (11879) |
|
| | | The information contained in this forum is from SpaForums.Com
and IS NOT AUTHORITATIVE advice or official commentary from SpaPartsNet or SpaBabes Incorporated. Use this information at your own risk! |
Note: Prices and Specifications subject to change without notice
|
|

|
|
|
|
Related @ SpaForums | CalSpa Model 6300 control issue... Update... 11/30/08
I took off the sides to reach the controls and it became all too (more)...
| Air Valve Replacement Beachcomber Tub Hi, I need to replace the air valve on my 2002 beachcomber 530.
While looking inside (more)...
| 3 dots flashing and already replaced the pressure switch Hi,
We have a PDC Spa, actually at one of our rental cabins, and several months ago, (more)...
| 3 dots flashing and alreay replaced the pressure switch Hi,
We have a PDC Spa, actually at one of our rental cabins, and several months ago, (more)...
| Spa pumps turn on and off Yes, when you turn it on it says FLO and the 1 pump that I turned on it's light was (more)...
| Circulation pump wiring issues. I purchased an E5 circulation pump, and the wiring instructions given to me said that (more)...
| Where to buy CalSpa Motor? Techies-
I recently replaced a 6HP pump on a CalSpa, because it had been making a (more)...
| ASI Manhattan Spa Hope you can help,
I've just got the above spa, the heating light has been flashing (more)...
|
|
|
Are you in the Tampa Bay area? Visit Our Store! 14413 N Nebraska in Tampa Florida!
| Copyright © 1997-2008 Spa Babes, Inc. Tampa, FL Sales: 1-866-364-9681 Tech Support: 1-813-235-4574 |
|
|